Results 1 to 10 of 16
Thread: extension cord
    Dec 2013
    Default extension cord
    I bought a Millermatic 211, the outlet in my garage is fed by 6 Guage wire,
    is it ok to use a 8/3 extension cord from 25' to 50'
    Thanks for any help
    4,461
    Yes it is ok, you could use a 12 cord with that machine.
    Sep 2009
    Colorado
    227
    Default Manual says 14ga OK
    The manual, on page 17, says that a 14 ga cord is adequate. Maximum length 53 feet. The maximum current rating is 25 amps.
    I figure that they must be taking into account the duty cycle of the welder, as a 25 amp load would usually require a 10 ga cord. This is all per the National Electrical Code, which has a welder exemption. Personally, I probably would use a heavier cord than 14ga.
    Richard
    Quote Originally Posted by tlhouston View Post
    Thanks for any help
    4,461
    The manual is for those fluent in code and nema. This machine may be ran on circuits to 50A provided the wire is a size bigger than the minimum,,,, with the 14 its 35A, with 12 or better 50A which is the plug comes on it. The unit has a 12 cord just to allow for it to use the larger circuit. It has its own thermal after the switch to protect it against overheat and for the finer wire within the unit. This will open before the unit will draw enough to overheat the incoming cord or even a 12 wire on a 50A.
    4,461
    The manual is terrible since this is marketed to a diy crowd, it should have lay language also and a recomentation above the code minimum which would get rid of confusion and no one thinks its a good idea to put this on a ******* 14 wire to a 50A recept.
    Wa
    633
    I totally agree sberry. It's funny how many threads get started on here asking basically the same exact thing. Miller should just say to run 25' use x gauge, to run 50' use x gauge, etc.
    Sep 2012
    AZ
    63
    Quote Originally Posted by raferguson View Post
    Richard
    The resistance of 106' of 14g is .268 Ohms. The voltage drop at 25A is 6.7V.
    The power dissipated at 100% duty cycle is 167W. However, the MM duty cycle at 25A input current is 30%. So, in practice, the cord would dissipate 50.1W or about 1 W per foot. What d'ya know! Those Miller guys was right! Moral: When all else fails read the manual. When that fails follow the manual
    Illinois
    632
    Yes, it is amazing how informative a manual is . Like instructions supplied with a product, when it doesn't fit or look like right, read the instructions.
    There are so many knowledgeable members here that they should be writing the manuals.
    Sep 2009
    South Carolina
    571
    "When all else fails read the manual. When that fails follow the manual"
    LOL, I'll be using that for the rest of my life.
    4,461
    The only problem with the manual in this case is that its not clear. It implies that this machine needs to be limited with a breaker of 35,,,, it does if,,,,, you use the minimum wire. Once you up the wire it can go on a common 50A welder circuit.