Hello All,
Just picked up my new welder and was going to start the installation of my electric service for the unit. I thought I could use 8 AWG like most normal 220 circuits, but I'm concerned that it may not meet the needs.
I will be putting in a dedicated branch circuit and it will be about a 35 foot run. Does anyone have experience setting up service for this welder? Would the 8 AWG get the job done or should I look at 6 AWG or larger?
Thanks in advance,
Mac
Results 1 to 10 of 18
Thread: Service supply lines
-
10-12-2012, 09:53 AM #1
Junior Member
- Join Date
- Oct 2012
- Posts
- 6
Service supply lines
Last edited by MacDuff; 10-12-2012 at 10:10 AM.
-
10-12-2012, 09:59 AM #2
And your new welder is a what??
-
10-12-2012, 10:00 AM #3
I am not familiar with the term AVG but I always use 6gauge wire. Seems to keep voltage drop down with and supply voltage more cosistantly. I use THHN.
Last edited by NathanH; 10-12-2012 at 02:22 PM.
Campbell Hausfeld 110V MIG
Jo Ann Fabrics Hot Glue Gun
-
10-12-2012, 10:06 AM #4
Junior Member
- Join Date
- Oct 2012
- Posts
- 6
-
10-12-2012, 10:09 AM #5
Junior Member
- Join Date
- Oct 2012
- Posts
- 6
-
10-12-2012, 11:38 AM #6
I use circuit breakers. You could use a slow blow fuse if that is what you have in your box. You could also get away with 8 gauge wire too. But might as well do 6 as you never know what the future holds for you as far as welders go.
Campbell Hausfeld 110V MIG
Jo Ann Fabrics Hot Glue Gun
-
10-12-2012, 12:32 PM #7
Yep at 35' you'll need #6 to cover your bases.
-
10-12-2012, 01:06 PM #8
Ed Conley
http://www.screamingbroccoli.net/
MM252
MM211
Passport Plus w/Spool Gun
TA185
Miller 125c Plasma 120v
O/A set
SO 2020 Bender
You can call me Bacchus
-
10-12-2012, 01:17 PM #9
Just in case you look at the manual and see odd wire gauge/CB recommendations:
50amp Circuit Breaker and Minimum #12 wire
This is due to the Duty Cycle of the machine. NEC allows for using smaller wire on a dedicated run and following the conduit/wire guidelines.
The Power cord is probably #12.
Anyhoo- as already mentioned if you use #6 you will definitely be set for any future machines, 100% for any machine that comes from the manufacturer with a 6-50 Plug on the end of the Power cord.
http://www.millerwelds.com/om/o316t_mil.pdfEd Conley
http://www.screamingbroccoli.net/
MM252
MM211
Passport Plus w/Spool Gun
TA185
Miller 125c Plasma 120v
O/A set
SO 2020 Bender
You can call me Bacchus
-
10-12-2012, 02:45 PM #10
Junior Member
- Join Date
- Oct 2012
- Posts
- 6
Thanks for all the input / responses. The manual is exactly what had me baffled. I may be in for more wiring than I planned as my box in the garage is on a 50 amp breaker and it looks like it was connected with 8 AWG. It's only money and time, right?