    Default Bobcat 225 NT died and will not do anything

    Yesterday I was using my Miller bobcat 225 NT as a generator, I had it hooked up to the meter loop of a shop I am building to check some electrical wiring I installed prior to getting electrical service. While actualy making sure some equipment worked in the shop, the Miller Bobcat died (no sputtering or hesitation it just died) while running at high idle, the machine would not do anything when I attempted to start.

    The battery is new, I have not checked because it was raining last night when this happened. The fuel tank is full and the oil level is good.

    Could this be a fuse, I read that the F-6 fuse when blown the welder would not start. Whould the blown fuse cause the machine to die and not even turnover?

    I need help?

  2. #2
    Join Date
    Oct 2004
    Location
    Edmonton, Alberta
    Posts
    7,447

    Default

    Well, yep, cause ther would be no power going to the coil. nor to the starter.

    Why it happened though is a dilema. Did you hook your supply power to test your circuits correctly? ie, it more sounds like you grounded one of the live circuits back to the frame of the machine. That would be the only reason I could think of to take out that fuse.

    There just may be further damage besides the fuse, as the DC system doesn't particularly like AC being pumped into it.

  3. #3
    Join Date
    Aug 2008
    Location
    Orange, TX
    Posts
    1,162

    Default

    If the starter solenoid doesn't even click, that's a pretty good sign fuse F6 is open. If it clicks but won't engage/turn over, check your battery as the charging regulator is probably bad.

    I doubt your testing hookup had anything to do with blowing F6 and I would check flashing diode D4 to see if it's shorted closed.
    MM200 w/spot controller and Spoolmatic 1
    Syncrowave 180 SD
    Bobcat 225G Plus LPG/NG w/14-pin*
    *Homemade Suitcase Wire Feeder
    *HF-251D-1
    *WC-1S & Spoolmatic 1
    PakMaster 100XL
    Marquette "Star Jet" 21-110

  4. #4
    Join Date
    Oct 2004
    Location
    Edmonton, Alberta
    Posts
    7,447

    Default

    There would have to be a heavy draw on the 12 VDC systom to open F6, like a dead short. I just guessed since you were powering an auxillary circuit when this happened, that that system could be the culprit, or it was simply coincedence.

    Never the less report back what you discover. Oh a dead battery, non charging, or low oil would not take that fuse out.

  5. #5
    Join Date
    Aug 2008
    Location
    Orange, TX
    Posts
    1,162

    Default

    I did consider the dumping of a heavy auxiliary power load while testing could result in a spike of exciter voltage which could take out (short) flashing diode D4 and backfeed the battery circuit thus blowing F6.

    But as you know, F1 should blow first if such were to happen so . . . ???

    I agree "a dead battery, non charging, or low oil would not take that fuse out" but a bad regluator could and I wouldn't rule out a battery/ignition circuit wire shorted to ground either.

    I too am curious as to what the OP finds.
    Last edited by duaneb55; 09-18-2012 at 08:24 PM.
    MM200 w/spot controller and Spoolmatic 1
    Syncrowave 180 SD
    Bobcat 225G Plus LPG/NG w/14-pin*
    *Homemade Suitcase Wire Feeder
    *HF-251D-1
    *WC-1S & Spoolmatic 1
    PakMaster 100XL
    Marquette "Star Jet" 21-110

  6. #6
    Join Date
    Oct 2004
    Location
    Edmonton, Alberta
    Posts
    7,447

    Smile

    I have my doubts that he is going to report back, most never do.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Function split() is deprecated in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/footer.inc.php on line 62

Welding Projects

Special Offers: See the latest Miller deals and promotions.

Warning: Function split() is deprecated in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/footer.inc.php on line 137