    Default Welding shop concrete thickness

    I did a 40' x 80' addition onto my existing shop, It is now time to pour the floor.
    My question is how thick should I make it.

    I will have semi trucks pulling inside, usually gravel trains for me to work on them which are empty, However I will also have the steel truck coming in to deliver once a week.

    I bought 6 x 6 x 6GA wire mesh to put in the floor, I plan on using a 6 bag mix which is 4000psi concrete.

    My hilo weighs 12,000 lbs plus the 7,000 lbs lift capacity which equalls 19,000 lbs. when fully loaded.

    I now have the sand compacted for the fourth time, ( watered down between compactions over a weeks time ) so the concrete will be about 6-1/4" deep.
    Keep in mind I'm using 6Ga. mesh verses the 10 ga.that is sold at the big box store.

    So my question is will the 6-1/4" be OK or should I go 8" in the area that the semi will pull onto and leave the rest 6-1/4" thick.

  2. #2
    Join Date
    Feb 2012
    Posts
    561

    Default Welding shop concrete thickness

    I have done some sidewalks in NJ that the city required 6", I would go 8" and have the concrete company add reinforcing fiber to the mix. I've done some concrete work, but I'm not a mason, just my .02
    Kevin

  3. #3
    Join Date
    Oct 2004
    Location
    Edmonton, Alberta
    Posts
    7,447

    Default

    In my concrete testing days, I'd go with a plastized mix as well. You can get varying hardness out of them. Talk to your concrete supply guys. That would be best as they know. Concrete just isn't mixing portland with gravel anymore. Also mix portland with your sand when you compact it. That'll take any moisture out of it to prevent any cracking of the concrete after it's poured. Wetting it down probably isn't the best. If your mixing it yourself you can still buy the plastizisor from a concrete firm. And if your using it, then the final product will last forever without cracking and its not nessesary to go the 8" either.

    Also remember to lift the mesh up off the ground, so the poured product can get undrneath it.
    Last edited by cruizer; 09-07-2012 at 07:26 PM. Reason: keys sticking on keyboard ack,,,

  4. #4
    Join Date
    Feb 2012
    Posts
    561

    Default Welding shop concrete thickness

    Commercial

    Most commercial concrete pours, such as retail stores, commercial offices, industrial buildings and warehouses, can need up to 9 inches of thickness in the concrete pad. Retail stores and commercial offices will call for at least 5 to 6 inches of concrete, while industrial buildings and parking lots can call for 7 to 8 inches of concrete. Any commercial parking lot that will have heavy machinery needs 8 to 9 inches of concrete thickness to withstand the heavy equipment.

    http://www.ehow.com/info_12163574_thick-pour-concrete.html

  5. #5
    Join Date
    Apr 2009
    Location
    Oswego IL
    Posts
    590

    Default Worked for a concrete company...

    first is the shop heated? How long will loads be parked, do you want to have to board all tracked equipment? If it were me I would not go anywhere less then 8 inches and would likely go thicker on the truck lane. If it were me, the center where the trucks and the load is would be 9 inches and I would taper to 6 inches in the corners and sides where the load is less. Also being a constant tempature is the best thing to keep the concrete from cracking.
    Kevin
    XMT 304
    Miller Spectrum 625
    Miller 30a spool gun
    S22a
    Miller Legend 302
    Lincoln LN25
    Ford f450 Maintainer Srv Truck

  6. #6
    Join Date
    Aug 2004
    Location
    Milan Michigan
    Posts
    1,670

    Default

    Cruizer, I'm not mixing the concrete myself, and yes I made chairs to hold the wire in the middle of the slab, I to have seen wire sitting at the bottom 1/2" of the slab on some jobs that I have torn out, plus I'm using the heavier wire.

    I didd'nt mention that I put 6 beam that are 30' long that are being cast into the floor with four beams running across the 6 beams. The beams cover an area that is 16' wide x 31' the beams are a combination 12" W.F. with a 10" flange and some 14" x 30lb.

    The top of the flanges will be flush with the finish floor and I shot them in with my lazer and they are all within 3/32" of being level.
    I put 2 of the beams inline with the frame rails of a semi truck, then the next two are 8'3" on center which catches the outside edge of a semi trailer and the last two are approx. 3' off each edge of a semi trailer to allow me to do a side pull.

    My plan is to be able to straighten out rolled over gravel train trailers, heavy equipment or what ever someone brings in to be straightened.

    When I'm not using it for straightening, I'll use it to fabricate off.

    The beams dont start untill your about 28' inside the door so I have decided to make the concrete 8" thick in the area leading up to the beams where the semi trucks will be and leave the rest 6-1/4"thick.

    In the new section of the building which is 40' x 80' I will have 2 crane bays with 2 bridges in each truck bay which is 4 cranes total.

  7. #7
    Join Date
    Sep 2005
    Location
    16919 Pole Rd. Brethren, MI 49619
    Posts
    4,376

    Default

    The duty cycle will be fairly low, 8 inches in critical spots should be fine, toss a couple rods in here and there.

  8. #8
    Join Date
    Apr 2009
    Location
    Oswego IL
    Posts
    590

    Default Nice Shop!!!

    Quote Originally Posted by Portable Welder View Post
    Cruizer, I'm not mixing the concrete myself, and yes I made chairs to hold the wire in the middle of the slab, I to have seen wire sitting at the bottom 1/2" of the slab on some jobs that I have torn out, plus I'm using the heavier wire.

    I didd'nt mention that I put 6 beam that are 30' long that are being cast into the floor with four beams running across the 6 beams. The beams cover an area that is 16' wide x 31' the beams are a combination 12" W.F. with a 10" flange and some 14" x 30lb.

    The top of the flanges will be flush with the finish floor and I shot them in with my lazer and they are all within 3/32" of being level.
    I put 2 of the beams inline with the frame rails of a semi truck, then the next two are 8'3" on center which catches the outside edge of a semi trailer and the last two are approx. 3' off each edge of a semi trailer to allow me to do a side pull.

    My plan is to be able to straighten out rolled over gravel train trailers, heavy equipment or what ever someone brings in to be straightened.

    When I'm not using it for straightening, I'll use it to fabricate off.

    The beams dont start untill your about 28' inside the door so I have decided to make the concrete 8" thick in the area leading up to the beams where the semi trucks will be and leave the rest 6-1/4"thick.

    In the new section of the building which is 40' x 80' I will have 2 crane bays with 2 bridges in each truck bay which is 4 cranes total.
    I want to see some pics, looks like a perfect setup

    Great idea to put the beams in the floor, are you going to cut chain pockets in the beams, how are you going to affix your pulling devices? I never been a fan of the d ring, it would be a lot of work, but 2" receiver tube would make nice flat floors, and be able to convert into pulling fictures.
    XMT 304
    Miller Spectrum 625
    Miller 30a spool gun
    S22a
    Miller Legend 302
    Lincoln LN25
    Ford f450 Maintainer Srv Truck

  9. #9
    Join Date
    May 2010
    Location
    Central CA
    Posts
    780

    Default

    For your floor beam, dig big footings and run rebar through the the beams.
    D ring on a heavy flat bar will work fine. Cut a big enough hole at the end of the beams to get the D rings in and out as needed, also the dirt.
    Think about a jib crane just heavy enough to swing a wire feeder.
    Pour the footing for the jib at the base of your gantry crane. Have the jib swing under the gantry.
    Run rebar from the beams in the concrete to a J bolt for the shop frame.
    That way the whole shop frame is grounded (HF tig) and you can hook your ground/ work lead to the J bolt and jig off the floor beams.
    Same for the welding table,a small pad in the concrete grounded to the frame, no cables under your feet.
    No saw cuts or cold joints in the bay you will use a creeper, nothing but smooth concrete.
    Last put your air compress on/off switch by the light switch at the mandoor exit, lights out, air off.
    Good Luck,
    Bob
    Millermatic 252 w/30A
    Big Blue Air Pak
    Ellis 3000 Band Saw
    Trailblazer 302 Air Pak w/ Wireless Remote
    8-RC
    Dynasty 200 DX
    XMT 350 MPa w/S-74 MPa Plus
    Millermatic 211
    Passport Plus
    Spectrum 625 X-TREME
    Lincoln SA-200 Blue Tint Red Face '63
    2-Lincoln SA-200 Red Face '68
    SA-200 Black Face '59
    SA-200 Green Lite '84
    SA-200 Green Lite '80
    SA-200 Red Face '69
    SA-200 Red Face '66
    SA-200 Green Lite '81
    Comming soon '70 Black Face Round Barrel

  10. #10
    Join Date
    Aug 2004
    Location
    Milan Michigan
    Posts
    1,670

    Default

    Thanks for the ideas, I have run rod to all of my crane columns already so yes I can have my ground connected to the table and it will all be grounded to floor beams also.

    As far as rebar, The beams are all welded together in a grid 6 going the 31' way and 4 going the oposite way all spaced apart.
    I welded mudd hooks to the bottom side of the top flange on all the beams.
    I have a little over 10,000 lbs of steel beams that the grid is built out of.

    No pockets for chains, I will just weld down to the beams as needed.

    No Jib crane will be needed because I'm installing 4 over head cranes in the building,

    I also have future plans to intall a 18,000 lb hoist so I will provide at least 12" of concrete where the posts will go.

    Thanks for the ideas, Keep them coming befor the concrete gets poured, I have all the mesh in so I'm waiting on the concrete guy now.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Function split() is deprecated in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/footer.inc.php on line 62

Welding Projects

Special Offers: See the latest Miller deals and promotions.

Warning: Function split() is deprecated in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/footer.inc.php on line 137