All I have right now is an electric drier outlet that’s not the same plug configuration needed for the MM180. So I bought a 6’ 10gauge 30 amp drier cord for a pig tail, connected the power outlet (wall receptacle) to it that the welding shop told me to use, My question is: is this all I need, to then plug in the 25’ 8/3 extension cord for my MM180 ? The MM180 cord is 12/3
Will this be safe to use..
Thanks
Fab Tech
Results 1 to 4 of 4
Thread: Electric Question
-
01-23-2008, 06:36 PM #1
Senior Member
- Join Date
- Jan 2008
- Location
- So. Cal
- Posts
- 100
Electric Question
-
01-23-2008, 06:59 PM #2
Well.....
The short answer to your question is: yes, it is safe.
The long answer: The friction connectors are susceptible to loosening and making a poor contact. Inspect your connectors regularly (under load, if possible) for signs of heat. Other than that, go on ahead.
Good luck.
Triggerman
Ammonia refrigeration tech
Trailblazer 302 (yes, it's new)
Millermatic 180 w/Autoset
CST-250
HF-15 High frequency
XR15 w/Push-Pull Gun
Victor O/A, DeWalt, North mask
"A professional knows what to do. A craftsman knows why."
-
01-25-2008, 06:35 PM #3
Junior Member
- Join Date
- Sep 2007
- Location
- Bosque Farms, NM
- Posts
- 10
My first career was as an industrial and commercial electrician. If the dryer receptical was all I had; that's exactly how I would do it. How ever, if access to the panel wasn't too much hassle, I would make a dedicated welder outlet. Perhaps a local electrician would trade out the work for some welding. Just my 2c.
-
01-25-2008, 10:44 PM #4
Senior Member
- Join Date
- Jan 2008
- Location
- So. Cal
- Posts
- 100
Thanks guys for your feed back, in the morning I’ll cut up some 1X1 tubing and fire up this pup, do a few tack welds and see how this works out. For my first welding project, it will be a welding cart, :-) Oh ya I’ll have photos too LOL.