    I have a Syncrowave 350LX Serial # KJ286672.
    Welder welds great when stick welding but when you break the arc and set the stinger down
    Within 10 to 20 seconds the breaker in the breaker box trips.
    Any ideas what may be going wrong with this machine?

  2. #2

    Default

    What is the breaker size and what amps are you welding at? AC or DC, rod size.....
    a-

  3. #3
    Join Date
    Oct 2004
    Location
    Edmonton, Alberta
    Posts
    7,741

    Default

    AS Andy said, it's likely that your breaker is too small and not handling the field surge after you break an arc

  4. #4
    Join Date
    Feb 2010
    Posts
    5

    Default my Syncrowave 350LX has Trouble

    breaker size dual pole 50
    amps 95
    DC
    rod size 7018 - 3/16

  5. #5
    Join Date
    Mar 2007
    Location
    Deltaville, VA
    Posts
    2,239

    Default

    What does your owners manual recommend for a minimum breaker size?

    125A?

    Don't just install a larger breaker using the existing wiring. The wiring needs to be sized according to the amp draw.
    Syncrowave 250 DX Tigrunner
    Dynasty 200 DX
    Miller XMT 304 w/714D Feeder & Optima Control
    Miller MM 251 w/Q300 & 30A SG
    Hobart HH187
    Dialarc 250 AC/DC
    Hypertherm PM 600 & 1250
    Wilton 7"x12" bandsaw
    PC Dry Cut Saw, Dewalt Chop Saw
    Milwaukee 8" Metal Cut Saw, Milwaukee Portaband.
    Thermco and Smith (2) Gas Mixers
    More grinders than hands

  6. #6
    Join Date
    Feb 2010
    Posts
    5

    Default

    Quote Originally Posted by SundownIII View Post
    What does your owners manual recommend for a minimum breaker size?

    125A?

    Don't just install a larger breaker using the existing wiring. The wiring needs to be sized according to the amp draw.
    the max Recommended Circuit Breaker is 150 I dont have a minimum breaker size. the wire is 6 6 6
    600 volts

  7. #7
    Join Date
    Oct 2004
    Location
    Edmonton, Alberta
    Posts
    7,741

    Default

    I guess you answered your own question then as 50 amps is barely enough power to run a little thunderbolt welder, let alone a biggun 350lx unit.

  8. #8

    Default

    50 amps isn't going to cut it. That's like jump starting your car with a lamp cord.
    I'm actually surprised it didn't trip the breaker sometimes when just turning the machine on from the transformer in-rush.

    As stated by Sundown, that machine likes over a 100 amp breaker and upsize your primary wire if needed.

    Good luck.

    A-

  9. #9
    Join Date
    Oct 2007
    Posts
    2,949

    Default Only 95 Amps?

    Quote Originally Posted by Hiteker View Post
    breaker size dual pole 50
    amps 95
    DC
    rod size 7018 - 3/16
    I'm surprised you even got the rod to light at all

    A 3/16" 7018 needs 200-275 amps to keep lit

    95 amps is good for a 3/32" 7018 or a 1/8" 6010/11
    "Bonne journe'e mes amis"

  10. #10
    Join Date
    Mar 2007
    Location
    Oahu, Hawaii
    Posts
    2,469

    Default

    Quote Originally Posted by ASKANDY View Post
    That's like jump starting your car with a lamp cord.
    A-
    lol..........
    I'm not late...
    I'm just on Hawaiian Time

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Function split() is deprecated in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/footer.inc.php on line 82

Welding Projects

Special Offers: See the latest Miller deals and promotions.