    Hi guys. New to posting but I have been lurking for years. I am going to try this area as well. I see that many of the newer 220v welders have a 110v outlet installed on them for coolers or grinders or whatever. How is this accomplished? I have looked at my Square wave 175 and there is no neutral wire. I would like to add a 110v outlet but I don't see an easy way. Thanks!

  2. #2
    Join Date
    Aug 2006
    Location
    N.C.
    Posts
    362

    Default

    A 220 is two 110 "legs" feed in.... not really a big deal..... using a multi meter connect your leads (from the meter) one to the center and one to the right / left prong of the receptacle and you will see 110 on each one..... just remember if you are welding and your buddy plugs up the grinder you will trip the breaker as the draw is on one breaker....plus (unless you add it) the 110 rep. wont have a fault protection and could let some magic smoke out
    George W. Bush was saving your butt whether you liked it or not!
    Fear is temporary, regret is forever
    HH210 with SG

  3. #3
    Join Date
    Dec 2008
    Location
    Lake Havasu City, AZ
    Posts
    4

    Default

    I don't need a neutral?

  4. #4
    Join Date
    Nov 2008
    Location
    N.Y.C
    Posts
    164

    Default

    To accomplish this their is a neutral in the machine which is what gets you the 110. So that means it's a 4 or 5(3 phase or single phase) wire setup,2 hots 1 neutral & ground or 3 hots 1 neutral & ground.

  5. #5
    Join Date
    Sep 2002
    Location
    Clark County, NV
    Posts
    2,696

    Default

    Yes, you need a neutral. Do NOT use a ground to return the unbalanced 120V from a grinder!

    The machines that have 120V available, without having a neutral wire in the plug, use a tap off of the transformer inside.

  6. #6

    Default

    Quote Originally Posted by MAC702 View Post
    Yes, you need a neutral. Do NOT use a ground to return the unbalanced 120V from a grinder!

    I'm not an electrician, but isn't it pretty standard to have the neutral and the ground tied together in the box? I don't see how it makes a difference.

    I'm not contradicting, I'm asking for clarification.
    Millermatic 180 Auto Set

  7. #7
    Join Date
    Nov 2008
    Location
    N.Y.C
    Posts
    164

    Default

    Quote Originally Posted by jweller View Post
    I'm not an electrician, but isn't it pretty standard to have the neutral and the ground tied together in the box? I don't see how it makes a difference.

    I'm not contradicting, I'm asking for clarification.
    It makes a huge difference. Neutral and ground are not the same thing,ground is for safety neutral is return to point of distribution. When you tie neutral to ground you potentially energize the machines chassis back on the ground and could knock yourself or someone else on their ass.

  8. #8
    Join Date
    Sep 2002
    Location
    Clark County, NV
    Posts
    2,696

    Default

    Quote Originally Posted by jweller View Post
    ...isn't it pretty standard to have the neutral and the ground tied together in the box...
    It is very important that they are tied together in one and only one location, the main service entrance. It is illegal and dangerous to tie them together in other locations. Older dryers and ranges with 3-prong plugs used to do this, as a cost saving measure, but that, too, was done away with long ago, and now they are four wires, even though two of them might go to the same bar in the panel.

  9. #9
    Join Date
    Nov 2008
    Location
    N.Y.C
    Posts
    164

    Default

    Quote Originally Posted by MAC702 View Post
    It is very important that they are tied together in one and only one location, the main service entrance. It is illegal and dangerous to tie them together in other locations. Older dryers and ranges with 3-prong plugs used to do this, as a cost saving measure, but that, too, was done away with long ago, and now they are four wires, even though two of them might go to the same bar in the panel.
    You're mistaken neutral and ground don't terminate at the service. Neutral comes from the utility company and ground is supplied by Earth(driven stake) or the water main(clamp). I also forgot building steel by cadweld or drill & tap.
    Last edited by Mr Bigs; 12-19-2008 at 08:47 PM.

  10. #10

    Default

    OK thanks guys. I know DC electronics pretty well, but AC is completely different.
    Millermatic 180 Auto Set

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Non-static method PhpQuickProfiler::getMicroTime() should not be called statically in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/pqp/classes/Console.php on line 77

Warning: Function split() is deprecated in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/footer.inc.php on line 62

Welding Projects

Special Offers: See the latest Miller deals and promotions.

Warning: Function split() is deprecated in /mnt/stor3-wc1-dfw1/357822/357839/www.millerwelds.com/web/content/lib/footer.inc.php on line 137