Hi guys. New to posting but I have been lurking for years. I am going to try this area as well. I see that many of the newer 220v welders have a 110v outlet installed on them for coolers or grinders or whatever. How is this accomplished? I have looked at my Square wave 175 and there is no neutral wire. I would like to add a 110v outlet but I don't see an easy way. Thanks!
Results 1 to 10 of 11
Thread: 110v outlet
Hybrid View
-
12-14-2008, 10:48 AM #1
Junior Member
- Join Date
- Dec 2008
- Location
- Lake Havasu City, AZ
- Posts
- 4
110v outlet
-
12-14-2008, 11:09 AM #2
A 220 is two 110 "legs" feed in.... not really a big deal..... using a multi meter connect your leads (from the meter) one to the center and one to the right / left prong of the receptacle and you will see 110 on each one..... just remember if you are welding and your buddy plugs up the grinder you will trip the breaker as the draw is on one breaker....plus (unless you add it) the 110 rep. wont have a fault protection and could let some magic smoke out
George W. Bush was saving your butt whether you liked it or not!
Fear is temporary, regret is forever
HH210 with SG
-
12-14-2008, 11:20 AM #3
Junior Member
- Join Date
- Dec 2008
- Location
- Lake Havasu City, AZ
- Posts
- 4
I don't need a neutral?
-
12-14-2008, 01:34 PM #4
Senior Member
- Join Date
- Nov 2008
- Location
- N.Y.C
- Posts
- 164
To accomplish this their is a neutral in the machine which is what gets you the 110. So that means it's a 4 or 5(3 phase or single phase) wire setup,2 hots 1 neutral & ground or 3 hots 1 neutral & ground.
-
12-16-2008, 11:05 AM #5
Senior Member
- Join Date
- Sep 2002
- Location
- Clark County, NV
- Posts
- 2,696
Yes, you need a neutral. Do NOT use a ground to return the unbalanced 120V from a grinder!
The machines that have 120V available, without having a neutral wire in the plug, use a tap off of the transformer inside.
-
12-19-2008, 12:24 PM #6
Member
- Join Date
- Jan 2008
- Posts
- 87


Reply With Quote