That's a no-no in any case. The neutral is a conductor. You would not want a conductor from the AC service to be electrically connected to a steel welding table.
Bonding a welding table to the building ground system is OK to do. If your table is bonded, then you should leave the ground from your 120V receptacles isolated. This prevents any possibility of a "dual" ground path.
Hank
Results 11 to 20 of 30
Thread: 110v Power on a Welding Table?
-
11-03-2008, 11:51 AM #11
...from the Gadget Garage
Millermatic 210 w/3035, BWE
Handler 210 w/DP3035
TA185TSW
Victor O/A "J" series, SuperRange
-
11-03-2008, 12:02 PM #12
Great comments - let me be more precise in what I want to do and the potential problem.
I have a stand alone MM 251, with plastic casters, on concrete floor, supplied with 230v grounded service.
I have a stand alone welding table mounted on rubber roller casters. When welding I clamp the negative lead from the MM 251 to my welding table. There would not be a case where the welding table would normally touch the 251, unless inadvertently - that could happen but not likely.
I want to mount two duplex receptacles on my welding table to serve light loads from my 4 1/2" and 7" hand grinders, and perhaps a light. These receptacles would be connected to a wall outlet with a 20 ft. extension cord.
If I connect the Green Ground wire from the 110v supply to the welding table (and I assume that I should in order to have a grounding connection to the hand grinders), am I going to have a problem also connecting the neutral welding lead to the table? The concern I have is that, in some way, by having a ground connection on the welding table, it will adversely effect the welder's circuitry.MTBob
____________________________
MM 251 w/Spool gun
MM 135
Evolution Cut Off saw
Logan Lathe
Clausing Mill
Walker Turner Drill Press
-
11-03-2008, 12:09 PM #13
-
11-03-2008, 12:51 PM #14
Senior Member
- Join Date
- Sep 2005
- Location
- 16919 Pole Rd. Brethren, MI 49619
- Posts
- 4,248
Bob, you describe your situation, just run the cord like you are planning.
-
11-03-2008, 12:51 PM #15
-
11-03-2008, 12:56 PM #16
Senior Member
- Join Date
- Sep 2005
- Location
- 16919 Pole Rd. Brethren, MI 49619
- Posts
- 4,248
If you use them feed from gfci circuit though as there is possibility of plugging a 3 wire tool in this kind of outlet.
-
11-03-2008, 01:04 PM #17
Senior Member
- Join Date
- Sep 2002
- Location
- Clark County, NV
- Posts
- 2,696
I was with you right up to there. The welder has no neutral, and in any case, like Hank said, the neutral (like on the 120V receptacles you are adding) is a conductor, not tied to ground except in the main panel.
I recommend a good heavy duty cord since I am assuming it will be on the floor in a semi-permanent basis.
There are no direct issues with having the ground from the 120V receptacles tied to the table (and they should be.)
-
11-03-2008, 01:11 PM #18
Haven't had too many problems when migging, or using stick with a auxillary ground hooked up to the tables, its with the Tig process then there will be some interferance.
We have had problems with a poor work clamp ground and thus literally smoking the auxillary ground back to the machine
So for the $6 bucks cost on a isolated ground duplex, why all the fuss.
-
11-03-2008, 05:56 PM #19
Senior Member
- Join Date
- Dec 2007
- Location
- Oklahoma
- Posts
- 641
-
11-03-2008, 06:30 PM #20
Senior Member
- Join Date
- Sep 2005
- Location
- 16919 Pole Rd. Brethren, MI 49619
- Posts
- 4,248
This is a strict code violation, this recept needs a ground wire hooked to it or it needs gfci, you cannot have an outlet where a grounded tool could be plugged in without a ground. Where those are used, such as hospitals and the pipe is metal, they are mounted in metal boxes they run an insulated wire for grounding.So for the $6 bucks cost on a isolated ground duplex, why all the fuss



Reply With Quote