Results 1 to 10 of 13
    Jun 2008
    Las Vegas,NV
    10
    Default Problem with 220
    I have a dryer outlet in the garage which i changed to the 6-50R for the welder. Its run to a 2 pole 30 amp square D breaker. It's a 4 wire set up. My problem is (amongst others) when i tested the outlet it only read 120 volts instead of the needed 220 for the welder. I tried looking up some kind of answer on search engines and the forum and couln't find any. Sorry if you've heard this before, but i'm totally lost. Any help is greatly appreciated.
    Thanks alot,
    Justin
    2,957
    Which 3- wires out of the 4 that were there did you use for the new 6-50r?
    You should disconnect the White at both ends and tape off - the Neutral is not used for the 240v 6-50R
    Jun 2008
    Las Vegas,NV
    10
    The black and red for the hots and the bare wire for the ground, the white is taped off and tucked away. I'm trying to locate the other end of the neutral at the box. Thanks for the quick reply.
    Justin
    2,957
    How did you take the reading?
    Jun 2008
    Las Vegas,NV
    10
    I tapped off both ends of the neutral still no luck. I used a solenoid voltmeter to get the reading and then i used a digital multimeter. reads 120 volts everytime.
    Justin
    East Tennessee
    143
    Measure it at the breaker...
    Professional Auto Mechanic since 1974
    My own shop since 1981
    Cya Frank
    Prairieville, Louisiana
    139
    Default Where are you taking your measurement?
    Where are you taking your measurement? You should have 120vac from ground to either hot . . And you should have 220vac from hot to hot if using a volt meter . . . make sure you are getting contact on the inside of your receptacle.
    On some heavy duty receptacles you have to really reach in with your probes to make contact. Sometimes on less expensive meters the probes are short . . . Also you have to remember a 220 vac receptacle is designed for a plug that will have 1/8" thick prongs, so you might be going in the middle . . . Wiggle around a little while watching your meter . .\My Flukes have no problem but my little Tripplet 310 does . . .
    As to using a WIGGY . . . I limit that to establish hot / no hot for quick safety check, not trouble shooting . . .
    Hope that helps . . . .
    Millermatic 251
    Lincoln AC/DC "Tombstone"
    Milwaulkee Grinder 4 1/2"
    Clark Grinder 4 1/2"
    East Tennessee
    143
    Did you check the voltage at the breaker yet?
    On some boxes you can plug the double pole breaker in, in an incorrect position & cause the problem you're having.
    Check & see what you have at the breaker.
    HTH
    Cya Frank
    Jun 2008
    Las Vegas,NV
    10
    I went to the panel checked everything and it turns out the breaker was faulty, I replaced it to see if that would help and there it worked. Thank you guys alot for your help, if your ever in the Vegas area I'll buy you a beer. Now it's off to buy my welder.
    Thanks again!
    Justin
    139
    Smile breaker guy . . .
    Quote Originally Posted by Frank865 View Post
    HTH
    The breaker guy got it . . . . I'm an "old" instrument tech . . . we are hard headed, we "check the loop" as a whole first . . . then trouble shoot backwards . . . but for power I think your source first (the breaker) is best way to go . . .
    Steve
    Millermatic 251