    Im looking to purchase a synchrowave 250 dx and would like to know if 100 amps will be enough to power the machine. I currently have 100 amp service in my garage.
    thanks, Tony

  • #2
    For a 220 welder you will need 200 amp service.

    Comment


    • #3
      You can find the info you are looking for in the 'service & support' menu at the top of this page. I run a Dynasty 300 off of 220 and a 50 amp breaker. Mind you, I don't use the machine above 200 amps, but the required breaker for the machine provides 65 amps at 60% duty cycle, using 250 amps welding current. If you have 100 amp service to your shop, than you should have nothing to worry about with the recommened breaker.

      Comment


      • #4
        you will need a 100 amp breaker for 220 single phase, I have a synchrowave 250 and know, I rigged for awhile on 2 50's but was told that was not safe, on a 50 and a 40, one would trip. Good Luck, Paul

        Comment