  • 240v engine drive receptacle

    I just don't get it. The engine drive also has the four blade receptacle. I have not used that fourth blade in any configuration. What is it for and when would you need it?

    I am making extension cords for the 211 and dynasty, they don't use it so should I just ignore it on the engine drive also?
    Attached Files

  • #2
    Yep. Those are 14-50R and I made an adapter to go from 14-50 to 6-50. I have all my machines running a 6-50 on single phase 240v. Just find the two hots and the ground. The 4th is a neutral. If you run 4-wire SO cord you can make a little portable subpanel and break out a 115v circuit to run a grinder or something. I don't know about the code supporting that use, but who knows. 240v runs all the power through the hots and the ground wire is just there in case there is a ground fault. That way the electricity can go somewhere intentional.

    Comment


    • #3
      "If you run 4-wire SO cord you can make a little portable subpanel and break out a 115v circuit to run a grinder or something."

      Ahhh, so that make's sense. Very good, thank you.

      Comment


      • #4
        As I understand it the 4th lug is used as the common/white for a 115 circuit. It was put there due to the newer appliances needing a 115 circuit as well as a 240 circuit.

        Please correct me if I'm wrong on this.

        Comment


        • #5
          You can make yer own adapter or buy one

          http://www.amazon.com/Hobart-770674-.../dp/B003J8NMF0


          Miller also has a version but more $


          the 14-50 receptacles also make feeding power to your house a lot easier

          Comment


          • #6
            Glad I could help. I cost me about $40 to make a 6ft conversion extension with 8ga. I had the the same day for abnout the same cost as oljne and no shiping. Whenever I take my welder to a new place with a different outlet I test the outlet and the make an adapter cord. It works well.

            Comment


            • #7
              If you have a rv place close they have some good 50 amp adapters 4 to 3 prong .

              Comment


              • #8
                Originally posted by Kpack View Post
                If you have a rv place close they have some good 50 amp adapters 4 to 3 prong .
                Those usually only provide 120 power from the 14-50 receptacle because there isn't anything on an Rv that is 3 wire 240v.

                They us the adapters for rigs that are 30 amp 120v but want to or need to use a 14-50 receptacle

                Comment


                • #9
                  Yes I didn't think about that . I usually make up my own on the welder . I forgot those rvs are from 50 amp to 30amp 120 v .

                  Comment